Buried cable

difowler1

Senior Member
Is it true that no single stranded wires can be direct buried without a raceway? Even if it is a triplex type cable. Only a cable similar to UF cable could be direct buried without a raceway.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector
Wrong picture.. that's SE, not USE. The NEC is a better reference than Home Depot :)
Refer to Art 338.12
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
UF is a cable type which is not offered in single-conductor form.
USE is both a wire and a cable type, in that it is available in both single conductor and multi-conductor forms, both of which are suitable for direct burial.
 