Burial Depths For Rigid Conduit

Status
Not open for further replies.

RATLIFF

Member
We Are Installing Conduit At A New Gas Station
Our Conduit Is Under 6" Of Concrete
The Inspector Rejected Our Installation Due To Depth Of Conduits
He Quoted 300.5 And Tells Me That The Conduits Must Be 24".
My Interpetation Of This Code Is That Under 2" Of Concrete That The Depth Only Needs To Be 6". We Are At An Impass And I Need Some Back Up.
Thank You
Greg

THANKS FOR THE REPLY
I WOULD THINK THAT THE 24" UNDER ROAD WAYS WAS DUE TO THE SURFACE BEING ASPHALT THE CODE DOES NOT SPECIFY CONCRETE OR ASPHALT
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The inspector is right. :mad: This is a Driveway and / or Parking Lot in reality.

Roger
 

celtic

Senior Member
Location
NJ
I would tend to agree with your inspector also....if your conduits are in the vehicle area, as opposed to a grassy area for signage, they would need to be at 24" ~ see 300.5....and as a "BONUS" check 514.8 Exception Number 2 (not quite apples to apples, but the intent seems to be there).
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
I remember where I learned that lesson. The Texaco station near the old aiport road off of Military Hwy in Norfolk Va., circa 1981. I had to cut the conduits off, take them out, hand dig down to 24" cover (let's not forget, it's 24" of cover, not 24" deep), lucky I was already at 18".
 

jdouglas

Member
Location
South Carolina
Driveway Parking lots

Driveway Parking lots

Ok We all know its 24" when you bury conduiot under a drive or parking lot.
So how deep and what is legal to use if I dont bury the conduit.
Im trying to feed a gate from another across a drive and I could dig up the 20" concrete or bore or many other things however I am not giving the inspector the pleasure of doing such. He is holding up a CO on a 50 unit complex because of 4 " and another thing doesnt mulch count for ground cover ?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
jdouglas said:
Ok We all know its 24" when you bury conduiot under a drive or parking lot.
So how deep and what is legal to use if I dont bury the conduit.
Im trying to feed a gate from another across a drive and I could dig up the 20" concrete or bore or many other things however I am not giving the inspector the pleasure of doing such. He is holding up a CO on a 50 unit complex because of 4 " and another thing doesnt mulch count for ground cover ?

I think you need a 4" high speed bump.
 

celtic

Senior Member
Location
NJ
I don't see where your arguement is....
"we know all it's 24" under a drive"...
"doesnt mulch count for ground cover" ...
What are you proposing? Mulch on a drive as cover???

I think there may be more to the story than you tell us:
"I could dig .. or many other things however I am not giving the inspector the pleasure of doing such. He is holding up a CO on a 50 unit complex because of 4 " ..."

The EI is NOT holding up the CO over 4", you are.

JMO
 

radiopet

Senior Member
Location
Spotsylvania, VA
Ratliff,

Sad to say it looks like the inspector is right. I would venture to say someone looked at the TOP location in the table " All locations not specificed below " when in in fact it was listed below.

Now if you only went 6" because you hit solid rock and poured 2 inches of concrete over it and such then you might have an arguement but as it stands now the inspector is correct.

Wish we had better news for you....
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Ok We all know its 24" when you bury conduiot under a drive or parking lot.
So how deep and what is legal to use if I dont bury the conduit.
Im trying to feed a gate from another across a drive and I could dig up the 20" concrete or bore or many other things however I am not giving the inspector the pleasure of doing such. He is holding up a CO on a 50 unit complex because of 4 " and another thing doesnt mulch count for ground cover ?

He is holding up a CO...

I believe he is enforcing the law. Especially if no communication was made with the inspector prior to installation. Valuable lesson in how to spell a-s-s-u-m-e.
 

jdouglas

Member
Location
South Carolina
Didnt say inspector want right asked for solution

Didnt say inspector want right asked for solution

Im asking is it legal to run rigid across the drive, or do you have a simple solution other than diggin the pavement or boring under it?

And the mulch question was seperate. If you are burying conduit does mulch count as ground cover. Had no plans to mulch the drive.

Thanks
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Yes, you can run it above ground, but I'm sure this will be considered subject to physical damage (probably severe in that it will be driven over) :D

I know that wasn't a help, but unless you can get special permission from the inspector for some type of installation, 24" is the code.

Roger
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Cover is defined in Note 1, Table 300.5. It may be sufficiently ambiguous to include mulch. Personally I wouldn?t count on it.

Technically, the wiring method may be laid out on the ground with no cover at all; however you are then constrained to provide whatever protection, support, etc. otherwise required by Chapter 3. The ?main rule? of 300.4 is short and sweet and achieving adequate protection in a trafficked area is difficult especially if the wiring method is actually subject to regular physical contact.
 