Branch Circuits in Multiple Floors

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
No, the nec is silent on that as long as the circuit isn't overloaded. I assume you are talking about house panel circuits?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There is no limit as Dennis mentioned. We may have panels in the basement feeding equipment several floors above.
 