where in the code can i find the exact definition of "bonding" and "grounding". I know article 250 covers this subject, but sometimes I get lost between "bonding" and "grounding". Thanks
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: bonding/grounding

This issue is one of the major problems with the NEC. Most of what we and the NEC calls "grounding" is really "bonding". A task force has been appointed to study this issue for the 2008 code after myself and others proposed changing the term "equipment grounding conductor" to "equipment bonding conductor". This proposed change was rejected by CMP 5 on a very narrow margin, just one volt less that the required 2/3s majority. The proposals stirred a lot of interest in the subject and resulted in the appointment of a task force.
Don
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: bonding/grounding

Asside from what has already been said, here is my simplistic view.

If it is a GEC or the main electrode, it is grounding. Anything else is bonding. OK, you can flame me now :)

Personnaly, I like it to be confusing. Keeps the communist away. :D ;) :p
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: bonding/grounding

Originally posted by dereckbc:If it is a GEC or the main electrode, it is grounding. Anything else is bonding. . . Personally, I like it to be confusing.
Then perhaps we should switch the two terms, and call it a ?ground? only if it does not touch the ground. Let?s take our lead from the rules of football:
(1) If you catch a punt in your own end zone, and drop to one knee, you are ?safe.? They call that a ?touchback.?
(2) But if you are forced back into your own end zone and are ?touched,? they call that a ?safety!? :D
 

physis

Senior Member
Re: bonding/grounding

You're not alone shakenbake, I remember those days myself.

I haven't looked at your profile, are you shakin n bakin because you're in LA area Ca.
 

cripple

Senior Member
Re: bonding/grounding

The NEC has not defined the term Grounding. Grounding Conductor and Equipment Grounding Conductor are defined in Article 100.

It would appear to me that grounding should be defined as the action taken to ensure, permanent joining of the non?current-carrying metal parts of the electrical system, equipment, raceways, and other enclosures, which is the definition of Bonding, with some changes and could read as following:

Grounding. The permanent joining of metallic n on?current-carrying metal parts of equipment, raceways, and other enclosures to the system grounded conductor, the grounding electrode conductor, or both, at the service equipment or at the source of a separately derived system,[/ I] to form an electrically conductive path that ensures electrical continuity and the capacity to conduct safely any current likely to be imposed.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: bonding/grounding

I'll take the part of Benny. From Merian Webster dictionary

Grounding
Ground-ing
Function: noun
: training or instruction in the fundamentals of a field of knowledge.
 

hurk27

Senior Member
Re: bonding/grounding

Equipment Grounding Conductor
Bonding Conductor
Grounding Electrode Conductor

All three of these can be each other.
And to figure out what each one is you must follow the current path that might be imposed on each conductor.
this means if lighting were to strike a appliance then the EGC to that appliance would be a grounding conductor to earth through the GEC to the GE.
If there was a short in that same appliance then this same EGC would serve as a bonding conductor.
we have to remember that these conductors serve multiple roles and can be all three in one. This is true for the service neutral as it serves all three. a water pipe GEC also serves all three. so if we get into changing the name to "equipment bonding conductor, then will the lightning path thinking get lost in the shuffle?
I just think that the definition in artical 100 of these conductors could be alittle more defined to reflect this as a way to allow us to better understand what each purpose each serves, and that the same conductor can serve each purpose at the same time.

The confusion is not understanding which purpose/'s the wire is for at the time of installation. And to understand this one only has to know how to follow the current path of each kind of current that could be placed upon the conductor, and know where that current (fault current) is trying to return to Ie: transformer (source), Earth. (lightning strike)

[ October 14, 2004, 07:13 PM: Message edited by: hurk27 ]
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: bonding/grounding

Originally posted by hurk27: And to understand this one only has to know how to follow the current path of each kind of current that could be placed upon the conductor, and know where that current (fault current) is trying to return to i.e., transformer (source), Earth. (lightning strike)
Nicely put. ;) When things get confusing, I always think it is best to take everything back to the basics.
 

hurk27

Senior Member
Re: bonding/grounding

Thank's Charlie B. Coming from you, make's my head swell. Now I'll have to go out and buy a bigger hat. :D

I agree with you If we keep the basic's in our thinking when we lay out circuits, we can save ourselves allot of trouble down the road.
It was once said that a job is only as hard as you make it, so then came the phrase KISS which = "Keep It Simple Stupid"
 