Getting ready to start wiring for above ground pool. I talked to the inspector who said the Buster Crabbe pools have to be bonded differently. He said I have to take all of the resin caps off and bond each metal beam/rod on the pool. Pool is 15x30. Wondering if bonding every other as opposed to each and every one would do the same. Any suggestions?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Bonding for above ground pool

Is this because all of the metal parts aren't solidly connected together or is this just his requirement?
 

Jav

Member
Re: Bonding for above ground pool

It is because it is not solidly connected. The walls are steel but have a coating on them for protection. He said it was only these types of pools.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Bonding for above ground pool

Does this pool fall under the definition of a storable pool as described in Article 680? If so, than the rules in section III Storable Pools would apply and no bonding would be required if it met the other criteria for this section.
 