We have a battery backup install in a house with very little space and no mechanical room. Homeowner wants the unit in the bathroom. The unit will contain the main service feeders to the house, a 200 amp transfer switch, batteries, and an inverter. I'm wondering if this location will work or not? Thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If there are circuit breakers involved then it would be a violation

240.24(E) Not Located in Bathrooms. In dwelling units, dormitories,
and guest rooms or guest suites, overcurrent devices, other
than supplementary overcurrent protection, shall not be located
in bathrooms.
 