Article 625 Electric Vehicle Power Transfer System

Status
Not open for further replies.

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I’ve been reading the Gen3 wall manual and they spec out 90c rated wire.
The sentence in the manual is "If installing for maximum power, use minimum 6 AWG, 90° C-rated copper wire for conductors.
NOTE: Upsize conductors if necessary."

I don't understand why it mentions 90C rated wire, I'm not aware of any technical justification for it. But I'd be inclined to think that is referring to the temperature of the insulation, not of the overall wiring method. So 4/2 NM or 6-6-6 SEU would be OK.

Cheers, Wayne
 