In NEC2014. Is DC side arc fault detection required in ground mounted PV farms not connected to a building. Also, is it required on ground mounted arrays that have the AC tie in on a building.
Section 690.11 ?Arc-Fault Circuit Protection (Direct Current)?
Series arc-fault protection requirements for dc PV circuits were first introduced in NEC 2011. However, these requirements applied specifically to PV systems with a maximum system voltage greater than or equal to 80 Vdc, and with dc circuits on or entering a building. In NEC 2014, these requirements are expanded to all PV systems with a maximum system voltage greater than or equal to 80 Vdc, regardless of location. As explained in the ROP: ?PV arc faults in ground-mounted PV arrays can result in grass and brush fires. Such fires can result in deaths and significant property damage, which can be prevented with PV arc-fault protection.? Note that the arc-fault protective device must be listed for use in dc PV systems. The applicable product safety standard is UL 1699B, ?Photovoltaic (PV) DC Arc-Fault Circuit Protection.?