Thx, lugs rated 75. just was wondering since you can use 90 chart on thhn when in EMT.
Ron
Think of it like a chain rated for 90 pounds, connected to hooks that are rated for 75 pounds. What governs the strength of this hook-chain-hook assembly? The 75 pound rated hooks. You would need hooks at both ends that are also rated for 90 pounds, if you wanted to take credit for the chain's 90 pound rating.
This is also the case with the 90C vs 75C ampacity ratings. You need both wire and terminations to be 90C rated, if you want to use the full 90C rating. It is common for wire to be 90C rated, but rare for terminations to be 90C rated. Separately-installed connectors like split bolts and insulated splice blocks (e.g. Polaris) commonly carry a 90C rating which you can use in an otherwise-empty enclosure, but for lugs that are built as part of manufactured equipment, the equipment usually has a 75C rating, or possibly a 60C rating. Even if the lug is marked for 90C, the equipment it is in does not necessarily allow you to take credit for this. You can value-engineer your way around this rule if you connecting 90C-rated/75C-sized wire locally at the equipment on both ends, and then splice it in separate enclosures to 90C-sized wire for the majority of the run. I'm not sure when that value-engineering would be cost-effective enough to justify the separate enclosures/splices/extra complexity, but it exists as a solution in theory.
It is difficult to fit the following point in the chain/hook analogy, but the primary value in having 90C rated conductors, is that it gives you some headroom for your the ampacity adjustment and temperature correction calculations. These calculations don't need to be applied to terminations, just to the wire itself once it leaves the equipment and travels in the raceway or cable. You get to use the 90C rating, as opposed to the 75C rating, as the starting point for these calculations, which reduce the ampacity from the way the conductor is tested with not more than 3 conductors bundled together in a 30C ambient temperature. A 4th wire requires a bundling derate (now called ampacity adjustment). An ambient temperature higher than 30C also requires a temperature correction factor. The 90C rating gives you some headroom for these calculations, which you can use even if terminations require a 75C rating.