Afci breaker

Status
Not open for further replies.

jph320

Member
Location
Cinnaminson nj
Occupation
Electrician
Running a 2 pole 50a to feed a tankless water Heater, does it need to be a afci breaker or even gfci? Of course located in basement
 

tom baker

First Chief Moderator
Staff member
This is an area every electrician should know, and the answer depends on what code cycle you are on.
GFCIs are section 210.8
AFCIs are secction 210.12
Big difference between 2017 and 2020
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
This is an area every electrician should know, and the answer depends on what code cycle you are on.

As well as any applicable local/state amendments.

I guarantee you, an electrician in Wisconsin should not be asking about AFCI requirements from an electrician in North Dakota.
Different AHJ, different rules.

As a side note: this is partly why the forum encourages you to include your location in your profile.
 