Adding new apartments -meter question

Status
Not open for further replies.

Electrifyme

Member
Location
Nj
Occupation
Inside wireman
I have a job at an existing apartment building that has a 400 Amp service feeding an 8 meter bank. All have there own disconnect leading to a sub panel in each apartment. Only 5 meters were in use and the plan is to add 4 more apartments. How do I go about adding a 9th panel for this scenario? I assume a stand-alone meter for the 9th apartment but how do I run the main line from the 400 amp switch? Or can I run off the 8 meter bank that is there ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Can you install a tap on the load side conductors of the 400 amp switch? Do you have a photo of the existing setup?
 

Electrifyme

Member
Location
Nj
Occupation
Inside wireman
I will send picture when I am back at the job. That was my thought also to come off a tap, just wondering how common this is. It is my first job by myself just want to get all my ducks in a row and not fail inspections. Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It's common for situations like yours and when done correctly it will be code compliant.
 