#8 on 50 amp breaker

bcl

Member
Location
Garden Ridge, TX
Occupation
Electrician (Owner/ Operator)
Hey all, I was recently called upon to inspect some EV charger circuits at a car dealership installed by another contractor. They used #8 THHN on 50 amp breakers for some 14-50 twist-lock receptacles. The breaker terminal rating says CU/AL 60/75. Am I reading this correctly that it is rated 60 degrees for copper and 75 for aluminum? In which case, their wire is too small. Is there some provision I'm not aware of, it would be a lot of wire they'd need to re-pull. Everything is installed in EMT.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It means that as long as no other wire conditions or wire type ratings prohibit it, the 75C rating can be used.
The description on the breaker just specifies which conditions are accepted by the breaker itself.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
But it should be noted that putting #8 on a 50A breaker is only possible if this is wired using individual 75C rated conductors in conduit. So assuming that when you said "THHN", it is in fact in conduit, this is fine. If it had been run using NM cable, you are required to use the 60C rating column, in which case #8 is only good for 40A.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
But it should be noted that putting #8 on a 50A breaker is only possible if this is wired using individual 75C rated conductors in conduit. So assuming that when you said "THHN", it is in fact in conduit, this is fine. If it had been run using NM cable, you are required to use the 60C rating column, in which case #8 is only good for 40A.
SER and MC cable are 75C rated and fine. It is mainly just NM that is a problem. (Maybe also UF, I forget.)
 

farmantenna

Senior Member
Location
mass
I think the wire should be #6 because of the continuous load but I don't know the actual load. could be 30+- or 45+-. Everyone I've wired required #6
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
But it should be noted that putting #8 on a 50A breaker is only possible if this is wired using individual 75C rated conductors in conduit. So assuming that when you said "THHN", it is in fact in conduit, this is fine. If it had been run using NM cable, you are required to use the 60C rating column, in which case #8 is only good for 40A.
If this conduit were conduit underground the installation would be considered a wet location and would be a code violation to use standard THHN.

I think you’re also saying that all conductors must have an insulation rated for the lowest temperature rating for all conductors in the conduit, is this what code ask for?
 

NoahsArc

Member
Location
Illinois
Occupation
Residential Electrician
I think the wire should be #6 because of the continuous load but I don't know the actual load. could be 30+- or 45+-. Everyone I've wired required #6
Yes, I would personally always run #6 THHN for a 14-50R or "EV outlet", simply for futureproofing. I don't care if they pinky swear they're putting a 32A on it. Next year they'll get a new car with a 48A and won't think twice to use the same receptacle. You should size for the device as well as the wire, and if the device permits 50A size for 50, and if it's extremely common to have 48 continuous, size for 60.

That said, this is a car dealership, and we all know they're super trustworthy people whose pinky swears are worth their weight in platinum, so it's GTG...
 