Dsg319
Senior Member
- Location
- West Virginia
- Occupation
- Wv Master “lectrician”
I have 1 single phase 120volt (20amp OCPD) motor starter where the control for it is tapped from the line side of the contactor.
I have to run this class 1 control circuit back to the PLC to go through a relay to be controlled remotely from a PLC output.
Can I use 16AWG as long as the load does not exceed it’s listed ampacity. Or am I going to have to use 14AWG.
I read 725.45 (C) and I see that with 14AWG and larger I’m allowed to have a tapped conductor from the load side of the branch circuit as long as the rating of the OCPD does not exceed 300% of my conductors ampacity.
I have to run this class 1 control circuit back to the PLC to go through a relay to be controlled remotely from a PLC output.
Can I use 16AWG as long as the load does not exceed it’s listed ampacity. Or am I going to have to use 14AWG.
I read 725.45 (C) and I see that with 14AWG and larger I’m allowed to have a tapped conductor from the load side of the branch circuit as long as the rating of the OCPD does not exceed 300% of my conductors ampacity.