When feeding multiple floating homes with feeders from shore, would you need a grounding electrode for each structure as you do per 250.32?
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Good question!
Some time ago I think there was a thread somewhat similar to this about oil rigs.
And If I remember they hung a ground rod in the water........,but who am I to say.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
When feeding multiple floating homes with feeders from shore, would you need a grounding electrode for each structure as you do per 250.32?

I would say no, 553.8 allows
(A) Grounding of Electrical and Nonelectrical Parts. Ground-
ing of both electrical and nonelectrical parts in a floating building
shall be through connection to a grounding bus in the building
panelboard.
To me that means you don't need to dangle a ground rod in the sea
 