In a wire way that contains both 50 hertz and 60 hertz circuits do they need to be divided? The 50 hertz is derived from a frequency converter
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

We're not allowed to tell non-electrical-pros how to do actually do wiring, but I'd say it should be no problem, as long as the insulation involved is all rated for the highest voltage.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
And since the 50 Hz is not coming from a utility service, it is likely that it is not necessary to uniquely mark the 50 Hz to distinguish it at all intermediate access points. But it would still be a good idea.