4x4 recessed junction box with 1-1/4" conduit

Status
Not open for further replies.

Shujinko

Senior Member
What is the smallest depth size for a 4"x4" wall recessed junction box in order to fit an 1-1/4" conduit on it? How about the depth for an 1-1/2" conduit? It's just to run AV and data cables in it, no wiring devices installed in the j-box just cables passing through.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Well, you have to fit the fitting and locknut, plus the wall-surface thickness.

I have found 4" deep ones:
 

jusme123

Senior Member
Location
NY
Occupation
JW
And how many boxes have each of us seen that where so stuffed with cat 6 cables they couldn’t put the cover on, looked like a blue bubble
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I don't think there's a legal minimum. As I said above, you have to fit the fitting and wall.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For 1.25" KO a 2 1/8" deep standard box will work if you can use a 4 11/16" box instead of a 4".
1.25 KO Box.jpg
 

kwired

Electron manager
Location
NE Nebraska
I think I would only do this if I were pulling straight through and only ending say 1-4 of the cables at that box.

No angle or U pulls in that small of a box. They don't even recommend that short of radius bending of the cable if you want maximum performance out of it.
 