320.23 Move

Status
Not open for further replies.

bphgravity

Senior Member
Location
Florida
1. 320.23 (330.23, 334.23)

2. Relocate text

3. Relocate all the text in 320.23(A) to 300.4. and between "where" and "run" the terms type AC, MC, and NM... Change 320.23, 330.23, and 334.23 to this new section location.

4. I just feel this requirement is in poor location as currently placed. Since the rule applies to more than one cable type, the requirement should be placed in the "general" requirement Article and then each cable method that must comply with that section can reference the general rule.

[ October 16, 2005, 05:45 PM: Message edited by: bphgravity ]
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: 320.23 Move

Problem: There are types of cables that do not have to comply with these requirements. Suddenly they would have to, with insufficient substantiation.

The rule's just not quite general enough. :)

Edit:
Since the rule applies to more than one cable type, the requirement should be placed in the "general" requirement Article and then each cable method that must comply with that section can reference the general rule.
But that's not the way it works - everything must comply with 300.4. The specific articles don't need to reference 300.4 for 300.4 to be enforceable. ;)

[ October 16, 2005, 11:50 PM: Message edited by: georgestolz ]
 

bphgravity

Senior Member
Location
Florida
Re: 320.23 Move

Originally posted by georgestolz:
Problem: There are types of cables that do not have to comply with these requirements. Suddenly they would have to, with insufficient substantiation.

The section will specify what cable sections apply so this wouldn't be an issue. For example (B) only applies to NM and ENT. They could add a new letter like (G).
 