I'm in the process of putting together pricing for my labor to install a 3000a main service with an MDP that will consist of 20-25 switches , as for the GES is 3/0 copper to the buildings water main and a ground rod sufficient or do I also need a 3/0copper to CEE as well

Sent from my SM-G965U using Tapatalk
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
250.66 to size the GEC to your metal water pipe. A #4 CU to the CEE would be fine. If you have building steel, you would also need a full sized GEC to that as well.
 

nickelec

Senior Member
Location
US
So building steel is usually tied in to the CEE to my understanding? So if I have this right

3/0 to water
#4 to CEE
3/0 to building steel
# 6 to ground rod (optional)

Sent from my SM-G965U using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes #3/0 is the largest GEC required, as noted certain electrodes allow smaller maximum sized GEC's. If you have the first three you can definitely skip the ground rods.
 

nickelec

Senior Member
Location
US
I'm also pretty sure that the room has to be a certain size and certain size egress I believe if the gears centered in the room 1 doors sufficient