300 amp commercial service

Status
Not open for further replies.

david f

Member
Location
florida
Occupation
electrician
What would be the best approach for feeding a 300 amp service on a garage? planing on putting a 325amp Continuous meter can with 2 150 amp panels. The service will be coming from the pole underground 180’ to garage location. would it be better paralleling feeders? If so what size aluminum conductors would be best considering voltage drop?
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
Are you sure the utility isn't responsible for running the service conductors to your meter?

Here's a voltage drop calculator.

If I'm reading it right, it says two sets of 3/0 AL would work. I assumed 3 phase at 240 volts.
 