Looking at a remodeled Deli wiring. In this building not separated by any firewall she has a Laundry mat and the new deli, Same owner running both location. Each building meter separate with One service lateral.
She needs 3-phase for her stove and I will have to come off the Laundry Panel since that is the only 3-phase panel. Since this is under same occupant, just different uses. Do I need anything special??
She mentioned Her buddy that another EC but can't get to her as soon as I can talked with inspector, and inspector said he needs an emergency Disconnect.
I can see how that would be nice.
Though since this is all under one owner ship I don't see a need for it. Since she has access to both panels.
Am I missing something.
I will be calling POCO to get load data to see if she can even power the 50 amp stove off that Panel.