What is the formula to calculate the inbqalance imposed on the neutral of a 3-phase system. I don't specify voltage since the formula will be the same just different digits to plug into it.

Jim
 

spsnyder

Senior Member
If your asking for the current in the neutral for an unbalanced system it is the square root of (Ia^2+Ib^2+Ic^2-IaIb - IaIc - IbIc).
 