250 kcmil SER Cable Clamp

Status
Not open for further replies.

Bama_Electrical

Senior Member
Location
Alabama
Occupation
Electrician
I am on a rough-in and the GC is requiring 250 kcmil SER cable. I can’t find any clamp connectors to fit that size cable. Standard 2” are too small. What do y’all use when bring you 250 into a panel?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
FWIW, Arlington has a 2" connector rated for up to 2.04" diameter cable, as well as larger sizes up to 4":


Their regular connector style (849S) only goes up to 2" trade size, which is limited to 1.75" cable diameter. Southwire 250 kcmil is 1.84" or 1.85" (3 conductor or 4 conductor), so I see that it wouldn't fit the regular style.

Cheers, Wayne
 