230.71(A) date

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
When did NEC 2014 Section 230.71(A) first came in NEC? I have very old switchgear and they cannot seem to install main breaker and wanted to know when this rule came so that they can grandfather already 7th spare service breaker in service switchboard that they are going to use to fed new loads without having to install main breaker
 

SSDriver

Senior Member
Location
California
Occupation
Electrician

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If you can show it was compliant when it was installed, you might be okay.

Or get (written) permission to use it from the inspecting entity.

There's another thread debating whether an unused seventh breaker must be removed.
 