If you have calculated a single phase 120/240 Volt, 18 unit multi-family dwelling load calculation at 277,104 VA for ungrounded conductors and 181,944 VA for grounded conductor (demands for stoves and dryers included)
Then 220.61 (B) (2) permits derating an ADDITIONAL 70% to the already reduced neutral ampacity if:
1. The calculated neutral conductor current is over 200 ampere and
2. The neutral conductor load is OTHER THAN NONLINEAR LOADS such as electric discharge lighting
My question is that every home is expected to have non linear load computers connected to the general purpose lighting load receptacle branch circuits or leds or fluorescent lights possible in the future so would applying an addition 70% neutral ampacity reduction be acceptable. We cannot know what loads will be served later but a service is installed now!
Or what if you have one small LED light bulb in a one closet? Would just one reactive non linear load stop you from being able to use this demand reduction?
Then 220.61 (B) (2) permits derating an ADDITIONAL 70% to the already reduced neutral ampacity if:
1. The calculated neutral conductor current is over 200 ampere and
2. The neutral conductor load is OTHER THAN NONLINEAR LOADS such as electric discharge lighting
My question is that every home is expected to have non linear load computers connected to the general purpose lighting load receptacle branch circuits or leds or fluorescent lights possible in the future so would applying an addition 70% neutral ampacity reduction be acceptable. We cannot know what loads will be served later but a service is installed now!
Or what if you have one small LED light bulb in a one closet? Would just one reactive non linear load stop you from being able to use this demand reduction?