210.63(B)(2) What is being required here?

Status
Not open for further replies.

ronmath

Senior Member
Location
Burnsville, MN
I understand what they want, just not sure how to achieve it when you only have one panel in a retail space? Or for that matter multiple panels in the same room?
 

tom baker

First Chief Moderator
Staff member
To me it says install a receptacle in the same room as the electrical service. If there is not a service panel in the retail space then no receptacle required, unless there is HVAC equipment per A
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If you have multiple panels, there's likely to be a 'house' panel, to which it should be wired.
 