Earlier I had the impression that with 2017 NEC the requirement for a grounding electrode at ground mount arrays would be eliminated with the deletion of 690.47(D), but looking at the new 690.47(A) I think the requirement is increased. A ground mount racking system is a structure and requires a grounding electrode system installed in accordance with Part III of Article 250. The relatively lax requirements of 250.54 Auxiliary Grounding Electrode, which I think satisfied 690.47(D), don't appear to suffice for the 690.47(A) GE, and it appears that the GE installed at the array must be bonded with the rest of the premises grounding electrode system. Am I correct? I was just surprised.