growler
Senior Member
- Location
- Atlanta,GA
There is no three phase panels in the Homeline series, it is however common to see multi-tenant units that have a 208/120 source divided into 208/120 single phase three wire feeds to each tenant and use single phase panels in each tenant space. You still have the 120 degree phase angle between the two ungrounded conductors. Ungrounded to neutral (120 volt loads) will still see 180 degrees between the two circuit conductors as this is truly a single phase section of the supply system and is reason a single pole AFCI wouldn't see any difference no matter which system it is supplied by.
Homeline and QO both are rated for 240 maximum, which 208 falls within the range. Only exceptions would be things like an AFCI that may have issues like mentioned in this thread. Standard thermal magnetic breakers will work fine on 208 volts.
We use larger frame breakers rated for 600 volts all the time for 208, 240, and 480 volts applications, they don't care what the voltage is as long as we keep it under maximum rating.
I understand what you are saying but after this problem come up I'm starting to wonder if this panel is allowed for 208y-120V. I know the regular breakers should work and you would think the arc fault single pole should work.
What I question is the rating of the panel. If you look at the panel all you will see is that it's rated for 240-120V.
Would it be Ok to attach a sticker that says the operating voltage is actually 208-120V?
I know that an electrician would measure the voltage but someone ordering and appliance may not.