Working on a remodel and the customer will have 2 gas tankless water heaters (1 on each side of the house). I know the AHJ will want the gas bonded at both water heaters. Any issues with having hot, cold and gas bonded together in 2 different places?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The gas line is normally bonded on the incoming (source) side of any CSST, and only once.

The appliance EGCs take care of any bonding of the appliance ends.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
You need to bond the copper piping at a single location. The is no requirement to install a bond to the hot water pipes or the gas lines. The hot piping gets bonded to the cold piping at the mixer valves. Steel gas piping gets bonded by the EGC of the appliance that could energize the piping.

As Larry mentioned if the gas piping is CCST you may have to install a single bond to the grounding electrode system depending which type of CSST is used.
 