2 piece emt connector

Status
Not open for further replies.

Kirk marcussen

New User
Location
Home
Occupation
Electrician
With a 2 piece emt connector, Is a egc needed to be run with the conductors, because of the lack of locknut and setscrew?
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
The inside part of the 2-piece is tapered and has sharp ridges that dig into the box or panel. So this performs the same function as the sharp points on the periphery of a locknut or the end of a set screw. Apparently this was effective enough to meet the requirements of the listing process Tom mentioned.
 

mikeames

Senior Member
Location
Germantown MD
Occupation
Teacher - Master Electrician - 2017 NEC
As indicated by synchro.

raco-conduit-fittings-2702-64_1000.jpg
 