15KV MV cable shield ground conductor size

Status
Not open for further replies.

marksemail

New User
Location
Tennessee
Occupation
Electrician
I am needing to size the shield grounding conductor for some 15KV 500MCM feeders I am installing. This conductor will be attached to the cable shield and go to ground. I will not be using this as an EGC. What NEC guideline will this fall under? I cant seem to find any standard directly related to shield grounding size in medium voltage applications.
 

jusme123

Senior Member
Location
NY
Occupation
JW
 

paulengr

Senior Member
Something I came across recently...


Apparently the high impedance of the foil shields is intentional. If you make it too conductive the shield has more losses than the cable itself. This totally makes me rethink concentric neutral cable vs a separate neutral. Also more or less proves it can’t be a ground.

There is a minimum cable size for power conductors in NEC but it’s rather obscure. It is in the ampacity table that shows a minimum along with a footnote. This applies to any wire in the power cable raceway and certainly applies to shield drains.

There is also a debated issue about grounding one or both ends. If you ground both ends it forms a complete circuit with the bonding so it can have currents induced on it. With only one end grounded this can’t happen. There is a minimum length where grounding one end only is the best way then after that point both ends since impedance is high enough it’s better to have the extra ground for voltage control.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I am needing to size the shield grounding conductor for some 15KV 500MCM feeders I am installing. This conductor will be attached to the cable shield and go to ground. I will not be using this as an EGC. What NEC guideline will this fall under? I cant seem to find any standard directly related to shield grounding size in medium voltage applications.
I curious as to what your calling “shield”.
Is it tape shield, or the 14awg (10awg?) wires concentrically laid around the cable?

If it’s concentric neutral cable is it full neutral or one-third neutral?
 