SPARKLEY
- Denver, CO
- Electrician
In a 200amp Nema1 MCB loadcenter, the CU Service Entrance Conductors coming from the meter housing were poorly installed and contorted. One main lug was bent outward and appeared to me to be under extreme tension (a side view would've better shown the bend angle of the lug, but see the leftmost terminal). Doing this for 40 years, I felt there was risk of this lug connection breaking and the SEC shorting against the inside of the deadfront, which would then clear (or burn itself out) due to no OCP between the SEC and the utility grid. I also felt that the terminal was neither designed to bend, nor to be bent back into position, but was damaged and that bending it back into place could void the equipment listing.
I showed the customer the situation and I then recommended we replace both the offending SEC and the main breaker kit.
Other electricians at my company felt this solution was excessive, and that the lug should be bent back into position.
I’m asking you veterans to weigh in on 110.12(B):
Internal parts of electrical equipment, including busbars, wiring terminals, insulators, and other surfaces, shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners, abrasives, or corrosive residues. There shall be no damaged parts that may adversely affect safe operation or mechanical strength of the equipment such as parts that are broken; bent; cut; or deteriorated by corrosion, chemical action, or overheating.
Does the NEC allow for a bent part such as this to be repaired instead of replaced?