Based on T250.66, my GEC only needs to be #8 CU max based on #2 AL service conductors (very common in my area). Now let's say the ground rods are the only electrodes that I use.
Does that mean I only need to run #8 to them?
Or must I still use #6 to the ground rods based on 250.66(A)? It says "shall not required to be larger than #6 CU" which suggests that #8 is fine since it's the maximum size required by T250.66.
My gut instinct tells me the #8 is fine, but this has always confused me nonetheless.
{I'm purposefully not mentioning the rebar bonding because I don't have my '05 with me.}