Had to install a 50amp 240volt receptacle (non-dwelling) outdoors.
It will be used for what I am told cow milking equipment as it is at a 4H camp.

I did not gather the material for this job, I met a project manager there yesterday with the material all ready. One thing I noticed was they had gotten just a standard 50amp breaker.

The way I read it, it should be a GFCI breaker. I don’t see any exceptions exempting us from that requirement.

If it were me I would have just went ahead and went the GFCI route the begin with, but before I bring it up to the big dogs I wanna make sure I’m not overloooking anything.

Am I missing something?
 
Last edited:

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
Had to install a 50amp 240volt receptacle (non-dwelling) outdoors.
It will be used for what I am told cow milking equipment as it is at a 4H camp.

I did not gather the material for this job, I met a project manager there yesterday with the material all ready. One thing I noticed was they had gotten just a standard 50amp breaker.

The way I read it, it should be a GFCI breaker. I don’t see any exceptions exempting us from that requirement.

If it were me I would have just went ahead and went the GFCI route the begin with, but before I bring it up to the big dogs I wanna make sure I’m not overloooking anything.

Am I missing something?
Yes it should be GFCI.