Article 399 Wiring Method Ampacity Requirements
xptpcrewx
Power System Engineer
Las Vegas, Nevada, USA
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
Wondering if there are any ampacity requirements in the NEC for Outdoor Overhead Conductors Over 1000-V (Article 399)? Thanks in advance.
don_resqcapt19
Illinois
retired electrician
I believe the tables in 310.60 of the 2017 NEC apply to those installations. If you are using the 2020, the over 1000v ampacities are in Article 311.
xptpcrewx
The tables in 310.60 (or Article 311) are only for type MV cable. What about exposed/bare overhead conductors...
don_resqcapt19
Illinois
retired electrician
Then I guess the NEC does not have the required information. It does a very poor job with medium voltage installations.
Many look to the NESC for medium voltage installations.
xptpcrewx
Thanks don-resqcapt19, this was my initial feeling, but wanted to make sure I wasn't missing anything. If anyone else can chime-in on how to handle this, it would be greatly appreciated.