Class B ceiling install. Ceiling is sloped

Status
Not open for further replies.

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
I have a Garage with 80 x 80 flat ceiling. From the Bottom of Deck to 18 inches is Class B for Natural gas. I have no problems Here I can understand the 18 inches definition.

Problem is the Slope roof. Is it along the whole slope 18 inches. Or just 18 inches at the peak. I am install Trapeze at 24. Below peak. EMT where they will be below the 18 Inch Class B area.
 

Attachments

  • Explosion Proof Area under decking.png
    Explosion Proof Area under decking.png
    17.5 KB · Views: 10
  • Class 1 Div 2 Ceiling.png
    Class 1 Div 2 Ceiling.png
    31.2 KB · Views: 13
  • Explosion Proof Area under decking.png
    Explosion Proof Area under decking.png
    30.1 KB · Views: 12

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
To be honest, I have no idea what you mean about Class B in relationship to classifying your locations. Natural gas is Group D.

That said, the right-hand figure in your third diagram would be correct; i.e., the 18" would be measured from the peak. If properly ventilated, it may not need to be classified at all. See Table 511.3(D).
 

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
To be honest, I have no idea what you mean about Class B in relationship to classifying your locations. Natural gas is Group D.

That said, the right-hand figure in your third diagram would be correct; i.e., the 18" would be measured from the peak. If properly ventilated, it may not need to be classified at all. See Table 511.3(D).
Acuttally better said Class 1 Division 2 Class b was a term I learned in the early 90s Stuck with me
 