Objectionable current

Status
Not open for further replies.

malkasajy

Member
Location
Qatar
Occupation
Electrical Engineer
While measuring the current on the main grounding conductor of panelboards was found 0.5 - 1.5 A objectionable current.
Note that these panelboards have on downstream at least one control transformer with bonded neutral. How we can solve the objectionable current in such situation?
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
We really do need to know what conductor you are talking about. Is this panelboard the building Service Entrance? Is it the Grounding Electrode Conductor at the SE or is it current flow on an Equipment Grounding Conductor that is part of a feeder to a remote panelboard?

Look at 250.6
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
We really do need to know what conductor you are talking about. Is this panelboard the building Service Entrance? Is it the Grounding Electrode Conductor at the SE or is it current flow on an Equipment Grounding Conductor that is part of a feeder to a remote panelboard?

Look at 250.6
If it is the GEC of the main disconnect/service panel, then the nature of the POCO MultiplyGroundedNeutral system that some current will flow in the GEC. This is because the path through your Ground Electrode to the POCO Ground Electrode at their transformer is electrically in parallel with their neutral.
If it is the EGC between a subpanel and the service disconnect, then current there would be an indication either of a ground fault downstream which would trip a GFI if one were present OR a downstream connection between the grounded equipment and local earth (such as water piping or a separate (unnecessary and potentially harmful) ground rod required by an equipment manufacturer. To check this out you can put an amp clamp around all of the ungrounded lines going to the subpanel and check whether or not you see the same current as when clamping the EGC.
 

malkasajy

Member
Location
Qatar
Occupation
Electrical Engineer
The current flows on the GEC of subpanel. This subpanel has a circuit feeds a control panel. The control panel has a control transformer with bonded neutral at the secondary side.
 