I can't see where the NEC ever allows it in an "unfinished basement or crawl space" (as far as Romex smaller than #8).
Local jurisdiction may, of course, amend that
(C) In Unfinished Basements and Crawl Spaces. Where
cable is run at angles with joists in unfinished basements
and crawl spaces, it shall be permissible to secure cables
not smaller than two 6 AWG or three 8 AWG conductors
directly to the lower edges of the joists. Smaller cables
shall be run either through bored holes in joists or on running
boards. Nonmetallic-sheathed cable installed on the
wall of an unfinished basement shall be permitted to be
installed in a listed conduit or tubing or shall be protected
in accordance with 300.4.
Gus 334.15(C)
At what height can I staple nm ( romex ) to the bottom of floor joist in a basement of house rather than bore holes?
I thought we were saying the same thing
OP asked at what height.. I meant to answer "can't regardless of height"if its a crawl or unfinished basement...
I would go ahead and drill holes. Besides stapling perpendicular to the joists being a super mongrel installation, i find it much faster to drill rather than staple.
Yes! Boring holes is easier/faster than driving staples overhead or on my back. Plus you can bore any size hole for extra cables.
Yes, and some of us are faster at running raceway then installing running boards plus stapling cables to them. Usually looks neater as well.We are all so set in our ways, I think running boards are faster than drilling and threading cables.
We would square off the nm cable and run it close to the outer walls. Some we would be able to nail to the plate atop of the block wall while the others could be boxed in
That all depends on how many holes and cables we're talking about. Pulling multiple cables through a long run of holes is no picnic, especially if you get that NM cable that has the consistency of fine sandpaper.
I would normally drill holes in a basement because they may wish to finish the space one day but in a crawl space I would do whatever was the least amount of work.