Fire stopping

Status
Not open for further replies.

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Does a metallic electrical outlet box need putty pad when is install in a fire rated wall in both sides?

Are you referring to a through box where it extends from one side to the other. you can see through it to the other room.
No No pad necessary as you cannot have such a box in a fire rated wall in most instances.
Back to back boxes will need pad on one box at least depending on the rating of the wall.
 