What's the load line circuit breaker size for a Kohler 24RCL-QS for 120/240 VAC single phase 60 Hertz? This circuit breaker protects the wires from the generator to the automated transfer switch.
The generator's rated amps are 87 amps for natural gas and 100 amps for LPG.
Based on a 1.25 multiplier the load line circuit breaker should be 125 amps, but the spec and installation sheets don't say. Can anybody confirm what's installed from the factory?
The generator's rated amps are 87 amps for natural gas and 100 amps for LPG.
Based on a 1.25 multiplier the load line circuit breaker should be 125 amps, but the spec and installation sheets don't say. Can anybody confirm what's installed from the factory?