Setting delay time for ground fault protection

Status
Not open for further replies.

Magic Gorge

Member
Location
Lexington, KY
When determining the circuit breaker ground fault settings for two or more tiers, should there be any consideration for the time gap between the delay settings? For instance, if I set my main at 0.4 seconds and feeder at 0.3 seconds, the curve sheet shows no overlapping. However, should the feeder be set lower to avoid nuisance tripping?
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
When determining the circuit breaker ground fault settings for two or more tiers, should there be any consideration for the time gap between the delay settings? For instance, if I set my main at 0.4 seconds and feeder at 0.3 seconds, the curve sheet shows no overlapping. However, should the feeder be set lower to avoid nuisance tripping?

Check the tolerances on the devices. Make sure an overlap didn't creep up on you. Otherwise, 'Coordination' is defined as, 'Daylight between the curves'.