mcdow44
Member
- Location
- Silverdale Washington
I'm a Temporary Services Electrician in a Shipyard. We work to our Industrial Process Instruction along with the NEC. A typical setup for us would be running 5 sets of Single 8's (4000A) from the local 480VAC 3 ph ungrounded service point to our 4000A JBox to multiple 800A switches that would provide power for our load centers which could service blast equipment, etc. We install a GEC at our furthest upstream service equipment. Our definition for service equipment is the temporary service equipment downstream of the service point and includes a service disconnect and the very fist overcurrent protection device for the temporary distribution system. Our JBox does not fit this definition. Typically, I've seen a cable tied in to the service point ground to our JBox and then to our switch. Should this cable be sized as an EGC to be able to trip the 4000A setting at the service point or should this be sized as a GEC with a separate GEC at the 1st switch in line? I've seen it both ways. Also, with electricity wanting to go back to source, I'm curious how this applies on an ungrounded 3 phase system. I have seen poor crimps at the cable lugs where the cabling actually heated up and pulled out of its crimp. It didn't hit anything but if it hit the case of the metal Jbox and the Jbox only had a GEC, would it be able to trip the 4000A setting and would the size of the cable be able to handle it? We typically use 3/0 AWG for our GEC.