Any two conductors that are separated by a void will act as a capacitor, as will insulated conductors in close contact, and an insulated conductor in close contact with the external ground plane. The capacitors act as though connected in series. Thus, the one with the lowest value of capacitance (i.e., the one with the void in the middle, or the one not in close contact with its neighbor) will carry the largest value of voltage. This makes it the weakest link. A high voltage across a void will occasionally force a ?packet of charge? to cross the gap. This results in severe degradation of the insulation at that point, and makes it easier for the next packet of charge to penetrate the insulation. It is thus a self-accelerating failure mechanism. This test can be performed under load, but the connections must be set up in advance. Sensors are connected directly to the motor?s main power leads. Since the electrical frequency of the partial discharges is much higher than the motor?s 60 Hertz, a well-chosen set of filters allows independent observation of the discharges. As was the case with the current signature analysis (CSA), the operator must be trained in recognition and evaluation of the test results. A PD Test can also be performed off-line. This is the most effective test presently available for detecting voids in the insulation, and is the best available at this writing for evaluation of stator problems.