Ufer grounding

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Nothing in the NEC or most state amendments require the use of a Ufer (CEE) ground unless one already exists.
For a standalone PV system with panel(s), battery and DC luminaire, I am not sure that any ground is needed at all, if the voltage is low enough.
Add in an inverter to produce 120+ VAC and the picture changes.
Your AHJ may consider the pole to be a structure (though not a building) under the NEC.

Tapatalk!
 

iwire

Moderator
Staff member
Location
Massachusetts
I think light poles are exempted from the requirement to have a GE anyway.

Light poles have a direct exception allowing the disconnecting means of those structures to be located remote.

As far as the GE only structures supplied by more than one branch circuit require a GE.

:)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I misunderstood what we had. I thought there a pv system that fed lights on poles. I would think the pv system would need the ufer or grounding electrode but not the lights.

I am curious as to where the pv system is located?
 

iwire

Moderator
Staff member
Location
Massachusetts
I may be wrong but I think the OP is talking about these type of self contained PV street lights.

Solar-Powered-Lights.jpg
 