time delay relay schematic

Status
Not open for further replies.

greg furey

Member
Location
old lyme ct
hey all any help would be appreciated i am trying to wire up a simple time delay relay for a horn with a momentary on button i wire it up and works correctly the first time you apply 110 volts to the circuit but it won't cycle again unless u shut off the ckt and turh on again the paperwork with the time delay relay says that you need to remove the power and apply it again how do i do this thanks
 

Smart $

Esteemed Member
Location
Ohio
hey all any help would be appreciated i am trying to wire up a simple time delay relay for a horn with a momentary on button i wire it up and works correctly the first time you apply 110 volts to the circuit but it won't cycle again unless u shut off the ckt and turh on again the paperwork with the time delay relay says that you need to remove the power and apply it again how do i do this thanks
You may need time delay off relay.

Can you provide make and model of your time delay [on] realy?
 

greg furey

Member
Location
old lyme ct
time delay relay schematic

here is the make and model of the relay i have its a mcm electronics brand new this year 2014 part number 26-1960 its solid state and will take various control voltages but i am using 110 volts thanks
 

Smart $

Esteemed Member
Location
Ohio
here is the make and model of the relay i have its a mcm electronics brand new this year 2014 part number 26-1960 its solid state and will take various control voltages but i am using 110 volts thanks
Is this the one?

http://www.mcmelectronics.com/product/DISTRIBUTED-BY-MCM-26-1960-/26-1960

Manual: http://www.mcmelectronics.com/content/ProductData/Manuals/26-1960.pdf

Do you want to reset manually or automatically? If the latter, you have to get a time delay off relay, or scrap this one and get one that offers both time on and time off delay (pulse) operation.
 

greg furey

Member
Location
old lyme ct
time delay relay schematic

yes that is the correct relay in your post . i am trying to control a 120 volt horn for 30 seconds after pushing the momentary on button thanks resetting would have to be automatic
 

Smart $

Esteemed Member
Location
Ohio
yes that is the correct relay in your post . i am trying to control a 120 volt horn for 30 seconds after pushing the momentary on button thanks resetting would have to be automatic
If I understand the instructions correctly, setting operation mode C will give you power on start and delay off to timer setting...
 