Gfci location in commercial restaurant

Status
Not open for further replies.

macmikeman

Senior Member
If the op is referring to commercial kitchen receptacles , then yes all of them must have gfi protection, regardless of whether they are serving counter work spaces or are behind large fridges and the like.
 

iwire

Moderator
Staff member
Location
Massachusetts
If the op is referring to commercial kitchen receptacles , then yes all of them must have gfi protection, regardless of whether they are serving counter work spaces or are behind large fridges and the like.

I agree, but there is no NEC requirement to provide any receptacles.
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
So plan on putting in GFI breakers to make it readily accessible since the equipment will most likely make most of the receptacles in accessible.
 

kwired

Electron manager
Location
NE Nebraska
I agree, but there is no NEC requirement to provide any receptacles.

you had me wondering what you had been smoking for a bit there, but true there is no requirement to provide most any receptacle in a non dwelling application, but there are some required outlets depending on some conditions, and some of them would require GFCI protection.

However my guess is that is not really what the OP is asking, something tells me he really meant to ask which receptacles (if they exist) are required to have GFCI protection.

My best answer is to tell him to read 210.8(B) carefully, and that the answer will depend on which year of NEC is being used. 2011 NEC has eight places/conditions where GFCI must be used. First 5 or 6 are likely to apply to a restaurant, 6 and 7 are not as commonly going to be found in a restaurant, but maybe not impossible to find somewhere in a restaurant, number 8 is probably not happening in a restaurant.
 