can you run #8 parallel conductors for 24vdc

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
Maybe I'm missing something here and this actually doesn't pertain to the question but why does the drawing call for #8's to begin with? #10 thhn is rated for up to 40amps at 90C. #8 is rated at 55amps. Those power supplies are 40amps. I got to be missing something...
Terminal temperature and/or equipment rating limits conductor temperature to 75?C. Under NEC, see 110.14(C).
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
Maybe I'm missing something here and this actually doesn't pertain to the question but why does the drawing call for #8's to begin with? #10 thhn is rated for up to 40amps at 90C. #8 is rated at 55amps. Those power supplies are 40amps. I got to be missing something...

Voltage drop. At 24v, you don't have much headroom before it gets excessive. 3% is only 0.72v. Low voltage distribution can use HUGE conductors for relatively small loads.


SceneryDriver
 

hurk27

Senior Member
As another pointed out I see no NEC issue with paralleling until you get to the distribution board.

I also understand why they did it this way looks like it was to keep going if any one PS failed.

The 3 power supplies feed the same bus in the power distribution block one + and one - bus because these busses are fed from 3 different power supplies this would not be parallel. conductors as per NEC definition.

From the power distribution block you have two sets of #8's that land on two separate busses on the positive circuit, which is ok still not a parallel circuit, but heres the problem all the negatives all land on a single buss in this distribution board, this then would be a parallel circuit, if they would have split this negative bus like they did on the positive bus then there would have been no parallel conductors.

another problem I see.
It looks like each set of conductors going to this distribution board each have 2 4 amp fuses and one 60 amp fuse, depending upon the calculated load thats 68 amps of fuses per each #8, that would not provide overload protection for the second set of #8s between the power distribution block and the distribution board, they would only be protected for fault current.

Almost all electrical standards require you to protect conductors from overload in one way or another, one is at the supply end, two is at the load end, or three is a fixed load that is not likely to ever be changed or can be changed that can over load these conductors, these above #8's are being supplied with 120 amps of available current, the 68 amps of fuses will protect the positive side of these to 68 amps, but the negative side can still see the full 120 amps across the two parallel neg. conductors.

The cooling fans might be self protected from over load, but the question is if the X-BP racks are?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The PDF that had been included in Post #7 above has been removed, due to concerns over copyrighted materials. That PDF is the subject of most of the subsequent comments. Those comments are not going to make any sense to future readers, due to the removal of the PDF. The moderators have therefore decided that it was appropriate to close the thread at this juncture. If the OP, or anyone else, wishes to continue the discussion of this topic, we suggest starting a new thread, one that does not rely on the availability of the (now missing) PDF. You can post a link to this thread, if that will help you start the new discussion.
 