310.16 column 75C or 90C for calculating feeder siize

Status
Not open for further replies.

steve holt

Member
Location
Hawaii
Which column on 310.16 do I use for calculating a feeder size? The feeder is above 800A so I know I need to size the feeder to at least meet the overcurrent protection, but am I limited by the rating of the lugs at the termination points (breaker 75C) or can I use 90C column?
 

Smart $

Esteemed Member
Location
Ohio
75?C column value is the maximum. You can use the 90?C column values for adjustment and correction. Final ampacity the lesser of the two.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The reason why you must use the 75C instead of the 90 is because the temperature limitation on the terminals is generally 75C not 90C so you must size to the weakest link.
 

templdl

Senior Member
Location
Wisconsin
The only other place that I can think of with rererence to 90degC rated cable is with the applications n of 100% rated breakers. When apply 100% rated breakers at 100% you must use 90degC rated cable but sized for 75degC.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here is a nice graphic on temp. of lugs

ry%3D400
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
And just to confuse things more, there are some situations where the device terminal requires 90C or higher wire, but you are specifically prohibited from using that temperature for ampacity calculations. :(

Tapatalk!
 