Is it okay to daisy chain a 30 amp 240 volt circuit to multiple boxes? I have a customer that wants to be able to plug in his portable welder in many different locations. I looked through article 210 branch circuits and couldn't find anything that says no. Just thought I'd make sure before I did it.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As long as you have proper overcurrent protection, there's no difference from daisy chaining the 120v 20 amp outlets.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
As hard as it is to believe, I cant find anything in the code that will say no. As long as the breaker is a 30 amp its ok.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Because you have multiple receptacles on that circuit, you are now limited to a max of 80% of 30A for a given receptacle (210.21(B)(2)). Could be a problem with a 25A nameplated item. However, I don't know who would ever catch that violation unless it was plugged in at the time of inspection.

If you label them as Welder Use Only, you can even go with a larger breaker than 30A.
 