Stationary Generator under deck

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
They have not been allowed under decks in this area.
The distance from the structure seems to be based on the type cover the generator has.
 

Wilg

Member
Location
VA
We have allowed them if there is adequate distance from any openings in the home. Only under open decks of course, if the manufacturer specs permit.

I think the last install manual I saw stated 5 feet clearance to any wood framing.

Is there any NEC requirement here? Other than standard equipment clearance.
 
Last edited:

Hendrix

Senior Member
Location
New England
We have allowed them if there is adequate distance from any openings in the home. Only under open decks of course, if the manufacturer specs permit.

I think the last install manual I saw stated 5 feet clearance to any wood framing.

Is there any NEC requirement here? Other than standard equipment clearance.
We have the 5' clearance from combustibles and "openings" but if the deck is open I do not regard it as being "inside" the structure.
 