NYC amendments to the 2008 NEC:

NYC 2011 Electrical Code Technical Provisions


ARTICLE 334
Nonmetallic-Sheathed Cable: Types NM, NMC, and NMS
SECTION 334.10
Section 334.10 ? Revise to read as follows:
334.10 Uses Permitted. Type NM, Type NMC, and Type NMS cables shall be permitted to be used in
the following:
(1) One- and two-family dwellings.
(2) Multifamily dwellings, except as prohibited in Section 334.12.
FPN: See Section 310.10 for temperature limitation of conductors.
Subsection 334.10(A)(1) ? Revise to read as follows:
(1) For both exposed and concealed work in normally dry locations.
Subsection 334.10(B)(1) ? Revise to read as follows:
(1) For both exposed and concealed work in dry, moist, damp or corrosive locations.
Subsection 334.10(C)(1) ? Revise to read as follows:
(1) For both exposed and concealed work in normally dry locations.
SECTION 334.12
Subsection 334.12(A)(1) ? Revise to read as follows:
(1) In any multifamily dwelling exceeding three floors above grade.
Subsection 334.12(A)(1) ? Delete the Exception in its entirety.
Subsection 334.12(A)(11) ? Add a new subsection 334.12 (A)(11) to read as follows:
(11) In non-residential buildings.


SECTION 334.15
Subsection 334.15(B) ? Change reference from 300.4(E) to 300.4(F).
SECTION 334.30
Subsection 334.30(C) ? Delete the subsection in its entirety


http://www.nyc.gov/html/dob/downloads/bldgs_code/electrical_code_local_law_39of2011.pdf
 